Solar Energy Battery Storage With Tesla Powerwall


Heads up, this is from Australia, but the same can be had in North America.

Solar Energy Battery Storage With Tesla Powerwall

$12499 for a 13.5 kWh system fully installed.

Each Powerwall battery pack is a self contained module consisting of battery cells, battery management system and an integrated AC/DC inverter. Mutiple Powerwall battery packs can be daisy chained together. The battery packs are connected to the meter board via an AC circuit. The battery packs will draw power from the AC circuit and start recharging when signaled by the Energy Gateway that the building is producing surplus energy and exporting to the grid. The batteries will discharge power into the AC circuit when signaled by the Energy Gateway that the building is importing energy from the grid. The building draws from the external grid when the Powerwall reaches its reserve.

Each Powerwall battery pack has a usable capacity of 13.5 kWh and a discharge rate of 5 kW continuous and 7 kW peak. Up to 9 Powerwall battery packs can be installed in a cluster.

The Powerwall has a 10 year warranty.





View user's profile
ehall
Super Nomad
****




Posts: 1906
Registered: 3-29-2014
Location: Buckeye, Az
Member Is Offline

Mood: It's 5 o'clock somewhere

[*] posted on 4-11-2018 at 06:40 PM


Interesting to see if the price comes down in the next couple years. Thats too big a nut for a lot of people
View user's profile
DavidT
Nomad
**




Posts: 494
Registered: 4-9-2005
Member Is Offline


[*] posted on 4-11-2018 at 08:35 PM




Tesla shows two 13.5 kWh Powerwalls for $12,500 with supporting hardware and typical installation cost from $800 to $2000.

Fun fact: In Florida by law grid tied solar panels without battery banks in homes must be shut down when the grid is down, like during and after the hurricanes last year. So even if they are functional and the mandatory grid disconnect switch is locked open you still can't use them.
And even if you install a full battery backed off grid capable system by law you must remain connected to the grid or you lose your certificate of occupancy.




David
Not one shred of evidence supports the notion that life is serious.
View user's profile
ehall
Super Nomad
****




Posts: 1906
Registered: 3-29-2014
Location: Buckeye, Az
Member Is Offline

Mood: It's 5 o'clock somewhere

[*] posted on 4-11-2018 at 09:13 PM


Quote: Originally posted by DavidT  


Tesla shows two 13.5 kWh Powerwalls for $12,500 with supporting hardware and typical installation cost from $800 to $2000.

Fun fact: In Florida by law grid tied solar panels without battery banks in homes must be shut down when the grid is down, like during and after the hurricanes last year. So even if they are functional and the mandatory grid disconnect switch is locked open you still can't use them.
And even if you install a full battery backed off grid capable system by law you must remain connected to the grid or you lose your certificate of occupancy.



Utility companies have a strong lobby.
View user's profile
tecatero
Nomad
**




Posts: 202
Registered: 11-20-2013
Member Is Offline


[*] posted on 4-12-2018 at 03:55 AM


be very interesting to see the " off grid" version,,,,,,,,,,Baja would be a great market to see if they hold up.......Looks like the Outback systems will have to do for a few more years
View user's profile
BajaTed
Senior Nomad
***




Posts: 859
Registered: 5-2-2010
Location: Bajamar
Member Is Offline


[*] posted on 4-12-2018 at 10:13 AM


Is below ground installation part of the powerwall spec. ???
Concern is physical security and optimal performance




Es Todo Bueno
View user's profile
mtgoat666
Select Nomad
*******




Posts: 17294
Registered: 9-16-2006
Location: San Diego
Member Is Offline

Mood: Hot n spicy

[*] posted on 4-12-2018 at 10:26 AM


Quote: Originally posted by ehall  
Quote: Originally posted by DavidT  


Tesla shows two 13.5 kWh Powerwalls for $12,500 with supporting hardware and typical installation cost from $800 to $2000.

Fun fact: In Florida by law grid tied solar panels without battery banks in homes must be shut down when the grid is down, like during and after the hurricanes last year. So even if they are functional and the mandatory grid disconnect switch is locked open you still can't use them.
And even if you install a full battery backed off grid capable system by law you must remain connected to the grid or you lose your certificate of occupancy.



Utility companies have a strong lobby.


the requirement to automatically shutoff solar power feed during transmission grid outage is to protect line workers. If the line is de-energized to allow safe work on lines, you need to prevent all the solar producers from energizing that line.

perhaps if batteries become more common a new safe disconnect system will come about?





Woke!

“...ask not what your country can do for you – ask what you can do for your country.” “My fellow citizens of the world: ask not what America will do for you, but what together we can do for the freedom of man.”

Prefered gender pronoun: the royal we

View user's profile
StuckSucks
Super Nomad
****




Posts: 2306
Registered: 10-17-2013
Member Is Offline


[*] posted on 4-12-2018 at 11:06 AM


Quote: Originally posted by mtgoat666  

the requirement to automatically shutoff solar power feed during transmission grid outage is to protect line workers. If the line is de-energized to allow safe work on lines, you need to prevent all the solar producers from energizing that line.


I learned this the hard way at the office. We are totally solar there, but LA City power went down outside, so we did too (for the reason mentioned). I'm optimistic that we will eventually figure a way to keep our building alive while protecting electrical workers outside.




View user's profile
ehall
Super Nomad
****




Posts: 1906
Registered: 3-29-2014
Location: Buckeye, Az
Member Is Offline

Mood: It's 5 o'clock somewhere

[*] posted on 4-12-2018 at 01:35 PM


Quote: Originally posted by StuckSucks  
Quote: Originally posted by mtgoat666  

the requirement to automatically shutoff solar power feed during transmission grid outage is to protect line workers. If the line is de-energized to allow safe work on lines, you need to prevent all the solar producers from energizing that line.


I learned this the hard way at the office. We are totally solar there, but LA City power went down outside, so we did too (for the reason mentioned). I'm optimistic that we will eventually figure a way to keep our building alive while protecting electrical workers outside.




Automatic transfer switches have been around for a long time. They are used on backup generators all the time.
View user's profile
Timinator
Nomad
**




Posts: 242
Registered: 6-27-2014
Member Is Offline


[*] posted on 4-12-2018 at 05:03 PM


So is the Inverter in these systems a 5KW Inverter with 7K peaks? What is the voltage of the system, 48V?
View user's profile
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8802
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 4-13-2018 at 04:27 AM


I'm sure its a slick looking box for the house

the inside is a bunch of littler batteries hooked together
(like a laptop battery)
with a built in charge controller and inverter



the voltage doesn't matter with something like this
because whatever you send to it it will convert it to what it needs
and give you 120v out






our website is:
http://www.mulege.org
View user's profile Visit user's homepage
mjs
Nomad
**




Posts: 305
Registered: 2-20-2013
Location: Off grid in San Felipe
Member Is Offline


[*] posted on 4-13-2018 at 08:31 AM


Battery voltage is approx 600 volts. One of the reasons it is only sod with professional installation.

For comparison, 13.5 kW is equal to a 24-volt, 540 amp-hour battery bank. A comparable 24-volt forklift battery (12-85-13, 810 ah) is about $2000.
View user's profile
Timinator
Nomad
**




Posts: 242
Registered: 6-27-2014
Member Is Offline


[*] posted on 4-13-2018 at 09:17 AM


So are the solar panels that you'd connect to this proprietary or can you use normal panels. Then....if normal panels, you could hook them up either 12, 24 or 48 and "it" would take care of the rest??
View user's profile
LukeJobbins
Nomad
**




Posts: 196
Registered: 3-11-2014
Location: Lemoore, Ca
Member Is Offline


[*] posted on 4-13-2018 at 09:51 AM


This came out several years ago but Tesla was and probably is still having financial issues. It was originally put out by Elon musk at a hotel conference years ago where he said it would be just over 2000 dollars to buy. The original goal was to even out the electric bills by having a smart battery that would charge during lowest rate periods and then switch to full battery use for the home during peak rate times. But while his thinking is top notch his financials are not. Tesla cars cost more than predicted by him. The solar tiles are more expensive than he said they would be. The battery is more expensive. He is an amazing innovator and his thinking is beneficial to humanity but people should be skeptical of his business practices. If Tesla goes down there is no one around right now to service or replace broken products. Most of Las Vegas is powered by his renewable energy technologies and if I am not mistaken most of his conferences are powered by the batteries. A few hotels around the world use them as well.
View user's profile
DavidT
Nomad
**




Posts: 494
Registered: 4-9-2005
Member Is Offline


[*] posted on 4-13-2018 at 09:59 AM


Tesla Powerwall 2 AC owners manual

Powerwall 2 AC Spec sheet

Powerwall 2 DC data sheet

Looks like it is 50 VDC in either the AC or DC Powerwall






David
Not one shred of evidence supports the notion that life is serious.
View user's profile
DavidT
Nomad
**




Posts: 494
Registered: 4-9-2005
Member Is Offline


[*] posted on 4-13-2018 at 10:21 AM


Quote: Originally posted by mtgoat666  


the requirement to automatically shutoff solar power feed during transmission grid outage is to protect line workers. If the line is de-energized to allow safe work on lines, you need to prevent all the solar producers from energizing that line.

perhaps if batteries become more common a new safe disconnect system will come about?



As I understand it it also has to do with the systems needing to synchronize with each other and the grid is the master with individual systems syncing to it.
With the grid down individual systems could sync with each other and cause problems when the grid comes online. All this in addition to protecting linemen from a live wire.
However I believe that you can lock out the master disconnect, going off grid, and still not be allowed to use your solar panels in your own house.
Unless you also have battery backup, then you can go off grid and use your system during power outages but you can't legally disconnect from the grid permanently.




David
Not one shred of evidence supports the notion that life is serious.
View user's profile

  Go To Top

 






All Content Copyright 1997- Q87 International; All Rights Reserved.
Powered by XMB; XMB Forum Software © 2001-2014 The XMB Group






"If it were lush and rich, one could understand the pull, but it is fierce and hostile and sullen. The stone mountains pile up to the sky and there is little fresh water. But we know we must go back if we live, and we don't know why." - Steinbeck, Log from the Sea of Cortez

 

"People don't care how much you know, until they know how much you care." - Theodore Roosevelt

 

"You can easily judge the character of others by how they treat those who they think can do nothing for them or to them." - Malcolm Forbes

 

"Let others lead small lives, but not you. Let others argue over small things, but not you. Let others cry over small hurts, but not you. Let others leave their future in someone else's hands, but not you." - Jim Rohn

 

"The best way to get the right answer on the internet is not to ask a question; it's to post the wrong answer." - Cunningham's Law







Thank you to Baja Bound Mexico Insurance Services for your long-term support of the BajaNomad.com Forums site.







Emergency Baja Contacts Include:

Desert Hawks; El Rosario-based ambulance transport; Emergency #: (616) 103-0262