Originally posted by DavidE
5,000 BTU 488 run watts 87% conversion efficiency factor of the inverter, limited by 50% amp hour drawdown limit on flooded lead acid batteries.
530 amp hours X2 = 1,060 amp hours 12 hours continuous. Ten GC-220 batteries dedicated to running the A/C only and absolutely nothing else. CEF losses
and total watt hours/day determine the size of the array. The presence of an MPPT controller, and wire line losses also must be factored. Same for
temperature compensation of the electrolyte for quiescent charge loss. Equalization adds to the panel capacity demand. There is always error in
theoretical workups.
All of this, meaning the chemistry going on in the battery, has to be understood and managed without overwhelming the end user. No one wants to be a
slave to a bunch of batteries, array of panels and an inverter. Guesswork means heartbreak, and disappointment coupled with a flat wallet. The user
has to be audited and the system has to be intelligently sized. Protection against salt air is crucial. It's not hard to do, but salt air will ruin a
system in months.
I've seen cloud edging utterly destroy a five hundred dollar controller in minutes. "But it was sized correctly!" was the wail from the installer.
Blanca is smart asking for help. A wrong solar system is worse than a hole to throw money in.
The ONLY WAY to determine the success of a system is if and when it delivers that maximum amount of service over the longest period of time, for the
least amount of money. |