BajaNomad
Not logged in [Login - Register]

Go To Bottom
Printable Version  
 Pages:  1  
Author: Subject: Question regarding electrical panel
Santiago
Ultra Nomad
*****




Posts: 3512
Registered: 8-27-2003
Member Is Offline


[*] posted on 2-26-2011 at 04:00 PM
Question regarding electrical panel


This used panel is going in my small off-grid cabin. I will run the hot from the inverter thru a 60am disconnect and to one of the hot buss bars.
1. Don't I run a wire to the other hot buss bar as if the black and red in the photo were tied together?
2. This panel has a small ground buss in the upper left hand corner; I can't remember if I'm supposed to tie that to the neutral buss (black arrows in the photo) or not and I get different info on the internets.
3. Came with two 20s and two 30s - aren't the 30s a little high for a small cabin - I was thinking of replacing them with 15s and using one of the 20s for the kitchen (all propane appliances). Are GFCI breakers the way to go or just use GFCI outlets in the kit/bath/exterior and run everything thru those?

[img]http://[/img]
View user's profile
woody with a view
PITA Nomad
*******




Posts: 15939
Registered: 11-8-2004
Location: Looking at the Coronado Islands
Member Is Offline

Mood: Everchangin'

[*] posted on 2-26-2011 at 04:19 PM


sorry. all i know about electricity is it is invisible and it hurts....

so, do'nt stand in a puddle when you tie in your GFCI's on the wet circuit!




View user's profile
msteve1014
Senior Nomad
***




Posts: 947
Registered: 12-2-2006
Member Is Offline


[*] posted on 2-26-2011 at 05:28 PM


Hi Santiago,
Yes, tie the two busses together if you only have 120 vac to feed it with.
You do not need to bond the ground and the neutral busses together.
Yes, 30 amps is probably more than you need, you would be better protected with the smaller breakers, and most likely you will never trip one of them if you are being careful about your power usage because of being on solar.
If you are going to buy a new breaker any way, check the prices on gfi breakers verses a gfi plug. They will both do what you want.

p.s. buy a ground rod if you do not have one yet, and bond everything to it.

[Edited on 2-27-2011 by msteve1014]
View user's profile
Santiago
Ultra Nomad
*****




Posts: 3512
Registered: 8-27-2003
Member Is Offline


[*] posted on 2-26-2011 at 05:37 PM


Thanks Steve: I also just realized that having a disconnect between the inverter and the panel is not needed - don't I just shut the inverter off?
I was going to make a ufer out of a 20' piece of #3 rebar (only size I ever see in BOLA) buried about 2' deep for ground - is this OK for ground?
View user's profile
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8813
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 2-26-2011 at 05:42 PM


the 60 amp breaker for the inverter is probably too big

most inverters are 33amp
so if you stacked 2 then the 60 amp would work

i'd run a 30 amp breaker on one

you can still run the 20 amp breakers

i would fill the box with breakers now...for use later
they are about 10 bucks each

do not connect the common and the ground
you could fry the inverter
remember the inverter is only circuit boards

edit...make sure you mark all the breakers
you will forget what's what later


[Edited on 2-27-2011 by Bob and Susan]




our website is:
http://www.mulege.org
View user's profile Visit user's homepage
woody with a view
PITA Nomad
*******




Posts: 15939
Registered: 11-8-2004
Location: Looking at the Coronado Islands
Member Is Offline

Mood: Everchangin'

[*] posted on 2-26-2011 at 05:42 PM


deeper. on this side it's 5 feet deep. but that is 2010 code. prolly diferente in baja, where the draw is much less on the entire house.



View user's profile
msteve1014
Senior Nomad
***




Posts: 947
Registered: 12-2-2006
Member Is Offline


[*] posted on 2-26-2011 at 06:04 PM


With the power you will be using you could use one of your 30s as a main in the panel and forget the disco.
The ufer would be ok, but the deeper the better with the dry soil i'm sure you have. Drive a piece of re bar as far in as you can and tie on to that.
View user's profile
RnR
Senior Nomad
***




Posts: 836
Registered: 5-1-2010
Member Is Offline


[*] posted on 2-26-2011 at 09:00 PM


Don't forget - the breaker size determines the downstream wire size. Or vice-versa, the wire size determines the maximum size breaker. The intent is to trip the breaker before the wire overheats and possibly arcs or starts a fire.

So, that said, 15 amp breakers require a minimum of 14 ga wire, 20 amp/12 gauge, 30 amp/10 gauge. Change those 30 amp breakers to something smaller or you will have to wire everything with 10 ga wire!

Ex: 14 gauge wire is rated to carry a maximum of 15 amps without overheating. A downstream appliance could short, pull 25 amps, overheat the 14 gauge wire, and never trip the 30 amp breaker.
View user's profile
BajaBruno
Super Nomad
****




Posts: 1035
Registered: 9-6-2006
Location: Back in CA
Member Is Offline

Mood: Happy

[*] posted on 2-27-2011 at 12:33 AM


Good advise here. RnR says it right on choosing breaker sizes--it all depends on the load, which determines the wire size, which determines the breaker size. But, nothing says you can't use 14g wire and a 15 amp breaker for a 5 amp load. However, if the load is much higher (not likely in your solar cabin), then choose the right wire size first.

A GFCI won't work without a good ground. Woody and msteve1014's advise is good--drive that rebar straight down 8' or so and you should be OK. You can do that by slipping a heavy piece of pipe (with cap on end) over the rebar and slamming it down. Outlet GFI's are much cheaper than breaker GFI's and will protect regular outlets downstream. Don't use them on appliances--motors don't like them and it is unnecessary.

Whether the ground and neutral buss bars are tied together depends on the installation: main panel, yes; sub-panel, no. You are using a sub-panel as a main panel, so I don't know, but it's probably a crap shoot.




Christopher Bruno, Elk Grove, CA.
View user's profile This user has MSN Messenger
RnR
Senior Nomad
***




Posts: 836
Registered: 5-1-2010
Member Is Offline


[*] posted on 2-27-2011 at 06:58 AM


Quote:
Originally posted by BajaBruno

Whether the ground and neutral buss bars are tied together depends on the installation: main panel, yes; sub-panel, no. You are using a sub-panel as a main panel, so I don't know, but it's probably a crap shoot.


Tie them together.

According to the NEC (National Electrical Code), all "separately derived power sources" are required to be grounded as close to the service entrance (usually the main panel) as possible. The inverter is a "separately derived power source" equivalent to a power company's step down transformer on a distribution line. IE: The source of the 120/240V power.

Household systems are to be grounded "at only one point". Usually the main panel. If a sub was connected and bonded, the nuetral and ground wires will provide TWO return paths for the electricity from the sub to the main and current will actually be flowing in both the nuetral and ground wires between the sub and the main. That is why main panels are connected and subs are not.

There is no real distinction between a breaker box designation as a sub or a main. It's just a metal box. The distinction is in how it is used and wired. That's why there is a green bonding screw for use in the nuetral buss supplied with every new panel and a tag that says something to the effect that "use this screw when equipment is to be used as "service equipment".
View user's profile
RnR
Senior Nomad
***




Posts: 836
Registered: 5-1-2010
Member Is Offline


[*] posted on 2-27-2011 at 07:03 AM


If anybody wants to know how and why a GFI works, just ask. It's a little complicated but interesting. They are not overload devices, (breakers).
View user's profile
1bobo
Nomad
**




Posts: 116
Registered: 2-5-2010
Location: Mulege
Member Is Offline


puzzled.gif posted on 2-27-2011 at 07:09 AM


Quote:
Originally posted by BajaBruno
Good advise here. RnR says it right on choosing breaker sizes--it all depends on the load, which determines the wire size, which determines the breaker size. But, nothing says you can't use 14g wire and a 15 amp breaker for a 5 amp load. However, if the load is much higher (not likely in your solar cabin), then choose the right wire size first.

A GFCI won't work without a good ground. Woody and msteve1014's advise is good--drive that rebar straight down 8' or so and you should be OK. You can do that by slipping a heavy piece of pipe (with cap on end) over the rebar and slamming it down. Outlet GFI's are much cheaper than breaker GFI's and will protect regular outlets downstream. Don't use them on appliances--motors don't like them and it is unnecessary.

Whether the ground and neutral buss bars are tied together depends on the installation: main panel, yes; sub-panel, no. You are using a sub-panel as a main panel, so I don't know, but it's probably a crap shoot.


Why do you say appliances don't like GFI's? Not questioning your expertise, but rather my assumptions.
View user's profile
cj5orion
Nomad
**




Posts: 336
Registered: 2-6-2010
Location: Pacific Beach/Gonzaga Bay
Member Is Offline

Mood: time for a cervaza !!!

[*] posted on 2-27-2011 at 08:05 AM


Quote:
Originally posted by Santiago
Thanks Steve: I also just realized that having a disconnect between the inverter and the panel is not needed - don't I just shut the inverter off?

Use the extra breaker for a main disconnect.
There are times.... when you'll use it.




Home Remodels/Builds..Recession!
Gone BAJA BUILDIN/FISHIN !
View user's profile
Santiago
Ultra Nomad
*****




Posts: 3512
Registered: 8-27-2003
Member Is Offline


[*] posted on 2-27-2011 at 09:13 AM
Is this how I make one of the 30amps a disco?


[img]http://[/img]

Believe it or not, I'm a general contractor but the only thing I know about 'lektrical is to hire a good electrician and then hope the inspector catches anything goofy. Of course, I DID have a cabin in Shaver Lake burn down following just this procedure.....
:(
View user's profile
wessongroup
Platinum Nomad
********




Posts: 21152
Registered: 8-9-2009
Location: Mission Viejo
Member Is Offline

Mood: Suicide Hot line ... please hold

[*] posted on 2-27-2011 at 09:22 AM


Of course, I DID have a cabin in Shaver Lake burn down following just this procedure.....


Santiago ...... still laughing...

[Edited on 2-27-2011 by wessongroup]




View user's profile
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8813
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 2-27-2011 at 09:37 AM


he question is...did you save "the box":biggrin:





our website is:
http://www.mulege.org
View user's profile Visit user's homepage
RnR
Senior Nomad
***




Posts: 836
Registered: 5-1-2010
Member Is Offline


[*] posted on 2-27-2011 at 09:43 AM


Quote:
Originally posted by Santiago
[img]http://[/img]

Believe it or not, I'm a general contractor but the only thing I know about 'lektrical is to hire a good electrician and then hope the inspector catches anything goofy. Of course, I DID have a cabin in Shaver Lake burn down following just this procedure.....
:(


No reason that this won't work.

Some cautions:

1. Might want to cover the exposed lugs/buss of the "A" side with tape or shrink wrap. Turning off the 30 amp/disconnect breaker to the "B" side still leaves those "A" side terminals hot and exposed.

2. Putting breakers in those "A" side slots to cover them and then using those breakers in the future may lead to turning off the disconnect and again leaving the "A" side breakers and circuits hot.

3. Do the next future owner a favor and put a note/tag on the breaker explaining the setup.
View user's profile
BajaBruno
Super Nomad
****




Posts: 1035
Registered: 9-6-2006
Location: Back in CA
Member Is Offline

Mood: Happy

[*] posted on 2-27-2011 at 11:52 AM


Quote:
Originally posted by 1bobo
Quote:

Why do you say appliances don't like GFI's? Not questioning your expertise, but rather my assumptions.


GFCI's are designed to protect people, rather than wire, by tripping in the presence of even tiny amounts of current traveling to ground, such as might happen if you touched a broken wire while you were grounded.

Some appliances create these tiny ground faults, either deliberately (such as a stove ignitor) or unintentionally (in a motor). They are not a shock hazard in a well designed electrical system, but they will give you annoyance trips with a GFCI, which is why your refrigerator is not plugged into one, and your garage has a single non-GFCI outlet for these type of appliances.

Most appliance manufacturers recommend against using GFCI outlets for their products. I hope this helps.
View user's profile This user has MSN Messenger
msteve1014
Senior Nomad
***




Posts: 947
Registered: 12-2-2006
Member Is Offline


[*] posted on 2-27-2011 at 11:57 AM


Quote:
Originally posted by Santiago
[img]http://[/img]

Believe it or not, I'm a general contractor but the only thing I know about 'lektrical is to hire a good electrician and then hope the inspector catches anything goofy. Of course, I DID have a cabin in Shaver Lake burn down following just this procedure.....
:(


No, run the hot from the inverter to the 30 amp c.b. Tie the two hot buss lugs together, like we were going to do any way. Now both busses are fed by the 30, and all the other spaces are switched by the 30 amp "main".

[Edited on 2-27-2011 by msteve1014]
View user's profile
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8813
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 2-27-2011 at 12:11 PM


why don't you get a better box with a place for a main cut-off

and then the breakers

cost about $30 usa at home depot includes breakers




our website is:
http://www.mulege.org
View user's profile Visit user's homepage
 Pages:  1  

  Go To Top

 






All Content Copyright 1997- Q87 International; All Rights Reserved.
Powered by XMB; XMB Forum Software © 2001-2014 The XMB Group






"If it were lush and rich, one could understand the pull, but it is fierce and hostile and sullen. The stone mountains pile up to the sky and there is little fresh water. But we know we must go back if we live, and we don't know why." - Steinbeck, Log from the Sea of Cortez

 

"People don't care how much you know, until they know how much you care." - Theodore Roosevelt

 

"You can easily judge the character of others by how they treat those who they think can do nothing for them or to them." - Malcolm Forbes

 

"Let others lead small lives, but not you. Let others argue over small things, but not you. Let others cry over small hurts, but not you. Let others leave their future in someone else's hands, but not you." - Jim Rohn

 

"The best way to get the right answer on the internet is not to ask a question; it's to post the wrong answer." - Cunningham's Law







Thank you to Baja Bound Mexico Insurance Services for your long-term support of the BajaNomad.com Forums site.







Emergency Baja Contacts Include:

Desert Hawks; El Rosario-based ambulance transport; Emergency #: (616) 103-0262