Hi. At Bahia now installing my new solar system. I have 8 100 watt 12volt panels going to an outback FM 80 flexmax controller and charging 6 105 amp 12 volt batteries. Everything is wired for twelve volts. Also a xantrex prosine 2000 pure sine inverter. Can I configure the panels for 24 volts to the controller but still keep the battery bank at 12? Or would I need to wire the batteries for 24 and get a 24 volt inverter? My distances are not critical so I can keep it at 12 with the wire I have. Just curious about the 24 volt configuration and if that would be beneficial. As it stands I will max my controller with two more panels if I stay at 12 volts whereas 24 volts has a lot of potential growth.
View user's profile
BigWooo
Senior Nomad
***


Avatar


Posts: 579
Registered: 1-2-2007
Member Is Offline


[*] posted on 10-10-2016 at 12:36 PM


Yes, with the FM80 charge controller you must wire the panels at a higher voltage than the battery bank for it to work properly With 12 volt batteries, the minimum voltage for the panels is 24 volts. Here's a link to the instructions for the FM80 charge controller. Read them very carefully. There's breaker and wire size minimums that must be adhered to. Read up on wiring, breakers, and maximum panel watts that can be hooked up to the controller.

FM 80 manual

Not @ edit. FM80 at 12 volts (battery bank) can have a maximum of 1250 watts worth of solar panels. You might want to even consider wiring the solar panels at 48 volts as there is less loss between the panels and the charge controller.

[Edited on 10-10-2016 by BigWooo]
View user's profile
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8813
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 10-10-2016 at 12:58 PM


i agree...bring the voltage down from the panels at 48v

let the controller change the voltage to your batteries...

you can always change your batteries later to 24v if you need a new inverter

solar.jpg - 57kB




our website is:
http://www.mulege.org
View user's profile Visit user's homepage
larryC
Super Nomad
****




Posts: 1495
Registered: 8-11-2008
Location: BoLA
Member Is Offline


[*] posted on 10-10-2016 at 04:07 PM


Definitely wire your panels to atleast 24v. My panels are wired to 90v in so I can use a smaller wire gauge. To take advantage of the growth potential of a 24v system you would have to change your battery bank and your inverter to 24v or even 48v to maximize the potential of your FM80 charge controller.



[Edited on 10-11-2016 by larryC]




Off grid, 12-190 watt evergreen solar panels on solar trackers, 2-3648 stacked Outback inverters, 610ah LiFePo4 48v battery bank, FM 60 and MX60 Outback charge controllers, X-240 Outback transformer for 240v from inverters, 6500 watt Kubota diesel generator.
View user's profile
wessongroup
Platinum Nomad
********




Posts: 21152
Registered: 8-9-2009
Location: Mission Viejo
Member Is Offline

Mood: Suicide Hot line ... please hold

[*] posted on 10-10-2016 at 04:46 PM


Thanks ... always good info from folks off the grid
View user's profile
ncampion
Super Nomad
****




Posts: 1238
Registered: 4-15-2006
Location: Loreto
Member Is Offline

Mood: Retired and Loving it

[*] posted on 10-10-2016 at 05:03 PM


Agree with Larry. The FM80 can take a max of 150 volts input (be careful, that is the Voc voltage not the Vmax) The higher the voltage the better.



Living Large in Loreto. Off-grid and happy.
View user's profile
larryC
Super Nomad
****




Posts: 1495
Registered: 8-11-2008
Location: BoLA
Member Is Offline


[*] posted on 10-10-2016 at 05:54 PM


If Voc of those panels is 17 then 8 in series would be 136v going into the charge controller. Awfully close to the 150v that Outback says will burn up the charge controller. I would probably wire them in 2 strings of four panels to give an input voltage of around 88v. Doug will have to look at the back of the panels and see what the Voc is for those panels. The panels I have have a Voc of 35v.
Larry




Off grid, 12-190 watt evergreen solar panels on solar trackers, 2-3648 stacked Outback inverters, 610ah LiFePo4 48v battery bank, FM 60 and MX60 Outback charge controllers, X-240 Outback transformer for 240v from inverters, 6500 watt Kubota diesel generator.
View user's profile
del mar
Banned





Posts: 1057
Registered: 7-23-2016
Location: the cantina of course
Member Is Offline

Mood: lil' fuzzy

[*] posted on 10-10-2016 at 08:02 PM


northern arizona wind and sun is your friend ;)
View user's profile
willardguy
Elite Nomad
******




Posts: 6451
Registered: 9-19-2009
Member Is Offline


[*] posted on 10-10-2016 at 08:25 PM


Quote: Originally posted by del mar  
northern arizona wind and sun is your friend ;)


bingo! :yes:
View user's profile
ncampion
Super Nomad
****




Posts: 1238
Registered: 4-15-2006
Location: Loreto
Member Is Offline

Mood: Retired and Loving it

[*] posted on 10-10-2016 at 09:17 PM


Quote: Originally posted by larryC  
If Voc of those panels is 17 then 8 in series would be 136v going into the charge controller. Awfully close to the 150v that Outback says will burn up the charge controller. I would probably wire them in 2 strings of four panels to give an input voltage of around 88v. Doug will have to look at the back of the panels and see what the Voc is for those panels. The panels I have have a Voc of 35v.
Larry


Again, agree with Larry. Most "12v" panels have a Vmax around 17v but the Voc is usually 20 - 21v . This would exceed the input rating of the FM80. Fortunately the cc will just shut down with no damage. Use two strings.

[Edited on 10-12-2016 by ncampion]




Living Large in Loreto. Off-grid and happy.
View user's profile
Doug/Vamonos
Nomad
**




Posts: 417
Registered: 6-19-2006
Location: Bahia de los Angeles
Member Is Offline


[*] posted on 10-11-2016 at 08:19 AM


Thanks everyone. I was hesitant because I didn't see anything in the manual specifically addressing "down converting". It does say it can do it but didn't expand on that. Time to go fishing. Yesterday toros were crashing the sardines on the beach right in front of geckos. Too much fun! Play with solar later.
View user's profile
Doug/Vamonos
Nomad
**




Posts: 417
Registered: 6-19-2006
Location: Bahia de los Angeles
Member Is Offline


[*] posted on 10-11-2016 at 01:11 PM


I set up two strings of 48 volts each and it seems to be working fine. Thanks.
View user's profile
larryC
Super Nomad
****




Posts: 1495
Registered: 8-11-2008
Location: BoLA
Member Is Offline


[*] posted on 10-11-2016 at 02:09 PM


Good for you, as long as none of the wires get hot and the magic smoke stays in the controller then you did good.



Off grid, 12-190 watt evergreen solar panels on solar trackers, 2-3648 stacked Outback inverters, 610ah LiFePo4 48v battery bank, FM 60 and MX60 Outback charge controllers, X-240 Outback transformer for 240v from inverters, 6500 watt Kubota diesel generator.
View user's profile
Doug/Vamonos
Nomad
**




Posts: 417
Registered: 6-19-2006
Location: Bahia de los Angeles
Member Is Offline


[*] posted on 10-14-2016 at 01:25 PM


I set up two strings of 48 volts each and it seems to be working fine. Thanks.
View user's profile

  Go To Top

 






All Content Copyright 1997- Q87 International; All Rights Reserved.
Powered by XMB; XMB Forum Software © 2001-2014 The XMB Group






"If it were lush and rich, one could understand the pull, but it is fierce and hostile and sullen. The stone mountains pile up to the sky and there is little fresh water. But we know we must go back if we live, and we don't know why." - Steinbeck, Log from the Sea of Cortez

 

"People don't care how much you know, until they know how much you care." - Theodore Roosevelt

 

"You can easily judge the character of others by how they treat those who they think can do nothing for them or to them." - Malcolm Forbes

 

"Let others lead small lives, but not you. Let others argue over small things, but not you. Let others cry over small hurts, but not you. Let others leave their future in someone else's hands, but not you." - Jim Rohn

 

"The best way to get the right answer on the internet is not to ask a question; it's to post the wrong answer." - Cunningham's Law







Thank you to Baja Bound Mexico Insurance Services for your long-term support of the BajaNomad.com Forums site.







Emergency Baja Contacts Include:

Desert Hawks; El Rosario-based ambulance transport; Emergency #: (616) 103-0262