Got it - final diagram and now we can start drinking


OK: black and white from inverter; green/yellow ties the ground and neutral busses; green to ufer ground and red ties the two hot busses together so they are both 110v. Throw the left 30 amp and everything to the right is disco. :cool:
[img][/img]

Bob - you're right, I'm just trying to use what I've got laying around in the shop until everyone who owes me money gets out of bankruptcy -- sheeesh.

Kinda funny how this got started: last spring SWMBO brings down a bunch of candles for lighting - OK, no problem. My fishing buddy and I go down in early October for a fishing trip and one evening I light all the candles, put on some latin jazz, pour a couple of glasses of WHITE wine and start making a pizza while my buddy opens a book. My neighbor comes over and remarks that it sure looks 'gay' in here.....5 minutes later we had both coleman lanterns on full blast, switched to blues/rock and Jack Daniels. Gotta nip these things in the bud.

[Edited on 2-27-2011 by Santiago]
View user's profile
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8813
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 2-27-2011 at 01:16 PM


i still say don't tie the ground to the common

a common feed still has some electricty and could fry the inverter

you ARE NOT "on the grid"




our website is:
http://www.mulege.org
View user's profile Visit user's homepage
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8813
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 2-27-2011 at 01:17 PM


i have one panel like that but i bought a double breaker for the main breaker

then the hot from the inverter to that and loop it

then both top and bottom strings are protected

[Edited on 2-27-2011 by Bob and Susan]




our website is:
http://www.mulege.org
View user's profile Visit user's homepage
msteve1014
Senior Nomad
***




Posts: 947
Registered: 12-2-2006
Member Is Offline


[*] posted on 2-27-2011 at 02:38 PM


Everything is protected by the 30 the way it is wired now, you do not need a 30 on each leg. Bob may be right about the bonding. There is no need to tie them together. The neutral can be left "floating". It is not a common practice, but some systems are wired that way to prevent "roaming" currents in sensitive electronic equipment.
View user's profile
wessongroup
Platinum Nomad
********




Posts: 21152
Registered: 8-9-2009
Location: Mission Viejo
Member Is Offline

Mood: Suicide Hot line ... please hold

[*] posted on 2-27-2011 at 02:56 PM






View user's profile
BajaGringo
Ultra Nomad
*****


Avatar


Posts: 3922
Registered: 8-24-2006
Location: La Chorera
Member Is Offline

Mood: Let's have a BBQ!

[*] posted on 2-27-2011 at 03:10 PM


Quote:
Originally posted by Bob and Susan
i still say don't tie the ground to the common

a common feed still has some electricty and could fry the inverter

you ARE NOT "on the grid"


I am no electrician but folks who are (and I know) tell me the same thing - keep the common and ground separate in the panel when the power is fed from an inverter.

Might be a good idea to check with a an experienced, licensed professional you know and trust to be completely safe on this one.

(My attorney made me say that...)



[Edited on 2-27-2011 by BajaGringo]
View user's profile Visit user's homepage
captkw
Ultra Nomad
*****




Posts: 3850
Registered: 10-19-2010
Location: el charro b.c.s.
Member Is Offline

Mood: new dog/missing the old 1

[*] posted on 2-27-2011 at 04:27 PM


why do I see more funky wireing,the older I get?????
View user's profile
BajaBruno
Super Nomad
****




Posts: 1035
Registered: 9-6-2006
Location: Back in CA
Member Is Offline

Mood: Happy

[*] posted on 2-27-2011 at 05:38 PM


Quote:
Originally posted by Bob and Susan
i still say don't tie the ground to the common

a common feed still has some electricty and could fry the inverter

you ARE NOT "on the grid"


After a little research, I see that Bob/Susan is sometimes correct. Some inverters (e.g. the Sunpower model) have the following warnings:

"The inverter must be connected to an AC equipment-grounding conductor directly and a DC grounding electrode conductor to a single point ground.

"The AC Neutral connection is for voltage sensing only and is not used as a current carrying conductor, nor is it bonded to ground."

Others, however (e.g. SureSine model), require that both the AC and DC neutral and the AC grounding wire are bonded to earth at the same place. This is the type I am familiar with.

Having been humbled, it seems that, once again, reading the manual is the best place to start. What kind of inverter is it, Santiago?




Christopher Bruno, Elk Grove, CA.
View user's profile This user has MSN Messenger
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8813
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 2-27-2011 at 06:15 PM


the "weakest link" and MOST expensive part is the inverter

protect that at all cost

it's like a lightbulb...it could go out at any time...then you're in trouble




our website is:
http://www.mulege.org
View user's profile Visit user's homepage
Santiago
Ultra Nomad
*****




Posts: 3512
Registered: 8-27-2003
Member Is Offline


[*] posted on 2-27-2011 at 07:40 PM


I don't have the inverter yet - but I notice that Midnight Solar shows that their e-panel has the ground buss and the neutral buss connected. I have a pdf file of it but can't figure how to post a pdf file. Trace's gagillion page installation manual is no help what so ever.
I'm going with the guy with the dachshunds as I'm a doxie guy - and I suspect he's living with his decisions. The green/yellow goes.
Thanks a lot for the info and opinions - it has helped. Now where's that white wine....
View user's profile
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8813
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 2-28-2011 at 06:01 AM


the work never ends...

biggerhose.jpg - 47kB




our website is:
http://www.mulege.org
View user's profile Visit user's homepage
durrelllrobert
Elite Nomad
******




Posts: 7393
Registered: 11-22-2007
Location: Punta Banda BC
Member Is Offline

Mood: thriving in Baja

[*] posted on 2-28-2011 at 02:09 PM


if you total the wattage of all light, appliances and other stuff on each circuit and divide by 120 volts you get the total amps being drawn for that circuit. the main amperage is the total watts of all circuits. even though most of the lights and appliances wil not be on all the time there only needs to be one time for all to be on to exceed the allowed ampacity of th circuit .
US Code only allows any circuit to be loaded 80 % of its rated load. , and to be sure there is absolutely no fire hazard, the 80% rule should be followed.

A 15 amp circuit with 14 gage wire can only be loaded with a total of 1440 watts,which is 80% of the 1800 watt maximum.

A 20 amp circuit with 20 gage wire can be loaded 1920 watts which is 80% of the 2400 watt maximum.




Bob Durrell
View user's profile
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8813
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 2-28-2011 at 03:25 PM


20 guage?

i'd put 6-10 guage

i guess no hairdryers if you use 15a breakers
some are 1500w

and then what about the times you need a toaster...
or
a breadmaker




our website is:
http://www.mulege.org
View user's profile Visit user's homepage
bajalou
Ultra Nomad
*****


Avatar


Posts: 4459
Registered: 3-11-2004
Location: South of the broder
Member Is Offline


[*] posted on 2-28-2011 at 04:44 PM


Quote:
Originally posted by durrelllrobert
A 15 amp circuit with 14 gage wire can only be loaded with a total of 1440 watts,which is 80% of the 1800 watt maximum.

A 20 amp circuit with 20 gage wire can be loaded 1920 watts which is 80% of the 2400 watt maximum.


Smaller wire for larger load????:?::?:




No Bad Days

\"Never argue with an idiot. People watching may not be able to tell the difference\"

\"The trouble with doing nothing is - how do I know when I\'m done?\"

Nomad Baja Interactive map

And in the San Felipe area - check out Valle Chico area
View user's profile
msteve1014
Senior Nomad
***




Posts: 947
Registered: 12-2-2006
Member Is Offline


[*] posted on 2-28-2011 at 05:10 PM


I think that was a topographical error.:lol:
20 amps= 12 gauge
Don't get all carried away with the calcs. If your on solar, you will probably be watching your amps and volts real close.
View user's profile
durrelllrobert
Elite Nomad
******




Posts: 7393
Registered: 11-22-2007
Location: Punta Banda BC
Member Is Offline

Mood: thriving in Baja

[*] posted on 2-28-2011 at 05:19 PM


Quote:
Originally posted by msteve1014
I think that was a topographical error.:lol:
20 amps= 12 gauge
Don't get all carried away with the calcs. If your on solar, you will probably be watching your amps and volts real close.

yep, typo. meant 12 gauge:rolleyes:




Bob Durrell
View user's profile
Bob and Susan
Elite Nomad
******


Avatar


Posts: 8813
Registered: 8-20-2003
Location: Mulege BCS on the BAY
Member Is Offline

Mood: Full Time Residents

[*] posted on 2-28-2011 at 06:00 PM


heat is a BIG factor down here

in the summer when its HOT the wire heats up and you should use BIGGER wire

don't discount this factor...we ain't in kansas anymore




our website is:
http://www.mulege.org
View user's profile Visit user's homepage
 Pages:  1  2

  Go To Top

 






All Content Copyright 1997- Q87 International; All Rights Reserved.
Powered by XMB; XMB Forum Software © 2001-2014 The XMB Group






"If it were lush and rich, one could understand the pull, but it is fierce and hostile and sullen. The stone mountains pile up to the sky and there is little fresh water. But we know we must go back if we live, and we don't know why." - Steinbeck, Log from the Sea of Cortez

 

"People don't care how much you know, until they know how much you care." - Theodore Roosevelt

 

"You can easily judge the character of others by how they treat those who they think can do nothing for them or to them." - Malcolm Forbes

 

"Let others lead small lives, but not you. Let others argue over small things, but not you. Let others cry over small hurts, but not you. Let others leave their future in someone else's hands, but not you." - Jim Rohn

 

"The best way to get the right answer on the internet is not to ask a question; it's to post the wrong answer." - Cunningham's Law







Thank you to Baja Bound Mexico Insurance Services for your long-term support of the BajaNomad.com Forums site.







Emergency Baja Contacts Include:

Desert Hawks; El Rosario-based ambulance transport; Emergency #: (616) 103-0262